UFTO Note - Superconducting Fault Current Limiter - Oct 15, 2004
| Wed, Feb 24 2010 11:23pm PST 1 | ||
|---|---|---|
|
Cleantech 706 Posts |
Subject: UFTO Note - Superconducting Fault Current
Limiter
Date: Fri, 15 Oct 2004
Australians quietly develop something completely different.
A "fault" in a transmission or distribution circuit is nasty
business. Circuit breakers open up, and that not only interrupts
service to a lot of customers, it can also put a surge on the
system. Worse, most fault clear themselves almost immediately,
and then a decision has to be made, either by a person or by the
equipment, whether and when to reclose the breaker. This is rough
on the system, and the breakers themselves are expensive and hard
to maintain.
A Fault Current Limiter (FCL) is a subtler way of dealing with
momentary faults. It recognizes a sudden high current that's not
supposed to happen; it "inserts" a high impedance in the line
momentarily to block that current, and returns to normal once the
situation corrects itself. This is not an easy task, however.
Currently (no pun), FCLs are far from ideal. Air core reactors
using metallic copper conductors incur high operational losses,
have limited response time, and wear out easily. What's more, the
breakers usually trip anyhow.
It's long been recognized that FCLs are a great application for
high temperature superconductors (HTSC). In fact, it's seen as
the first and best application of HTSCs on the power system. The
basic idea is to put a superconducting element in the circuit in
such a way that if too high a current comes along, the element
goes "normal" or momentarily stops being a superconductor. This
supplies the temporary high impedance to limit the current, and
once the current drops, the superconductor goes back to being a
superconductor and lets the current can flow again. This happens
almost instantaneously, faster than a mechanical switch, and with
"softer" transitions.
A SC FCL could thus detect abnormally high current transients in
the grid, e.g. from lightning strikes, in a fraction of a cycle,
and control the fault current so that system equipment can absorb
it safely, protecting valuable downstream infrastructure.
Superconductors go "normal" if the temperature gets too high, or
if the magnetic field gets too high. A SC FCL relies on the
latter type of "quenching". The base current passing through the
device produces a magnetic field below the level that would turn
off the SC -- a fault current will increase the magnetic field
enough to do the trick.
SC FCLs are the subject of intense R&D efforts worldwide. ABB
installed a prototype at a substation in Switzerland in 1997. The
DOE is funding a new $12M program
(http://www.engineeringtalk.com/news/nex/nex111.html), and EPRI
is offering a major study
(http://www.epri.com/destinations/product.aspx?id=439&area=10&type=2).
A conference earlier this month presented the very latest on SC,
including power applications. Note the three FCL sessions.
Applied Superconductivity Conf, ASC 2004, Jacksonville, FL,
October 3-8, 2004
http://www.ascinc.org/technicalprogram.asp
Essentially all these efforts to date are using the bulk property
of SC, and involve putting the entire load current through the SC
itself, as described above. This leads to designs that are highly
complex and which require a lot of SC material (i.e. very
expensive wire or tape - which is proving difficult to make in
large quantities). Moreover, none have progressed beyond the
R&D stage and or early field beta trials. (Note - in most
designs, a shunt actually supplies the impedance, not the
quenched SC element, -- even more complicated.)
Meanwhile, Down Under!
Meanwhile, a quiet development program in Australia has come up
with a novel approach which has already been successfully
demonstrated, and which is coming to North America. They
developed their own SC tape and SC coils (and manufacturing
method), and they invented and patented a 3-phase FCL that works
in an entirely different way. It is actually more of a
"controller" than a limiter of fault current.
It is a HTSC-enabled saturated magnetic core inductor. The load
current passes through a copper coil on one side of a
laminated-steel core. A DC coil on the other side maintains the
core in a fully saturated state of magnetization. The number of
copper turns are set so that a fault current in the AC coil will
drive the iron core out of saturation (on the negative swing of
the waveform). The coil then presents a large current controlled
reactance, clipping the fault current at the design value.
All of this is explained in detail in a white paper presented in
2003, and which is available on request. Download 3.5 MB --
(password required)
http://www.ufto.com/clients-only/clientdocs/SC.FCL.Techcon2003.doc.
The design uses only a small amount of superconductor, simply to
maintain the core magnetization (the only reason you need SC for
this is that ordinary coils would be too big and lossy). More
important, it works; it's simple, robust, and versatile; and it
will be available in a year at a reasonable price point. Key
advantages include:
Superior Fault Condition Performance
- Very fast response time – protection functions activate in a
fraction of a cycle.
- Large dynamic range – accommodates overloads without
degradation and recovers instantly.
- Superior dynamic performance – suppresses initial transients
more fully with much shorter decay times.
- Self-triggering/self-governing – operates instantly because of
fundamental physical laws, no external sensing or controls
required.
Low Cost
- Low operational cost – very little electrical losses in standby
mode.
- High durability – very low cycle fatigue - operates through
multiple operating cycles or fault events with little or no
degradation.
Flexibility
- Expandable architecture – can be field or shop reconfigured to
meet future requirements or changing grid characteristics.
- Small footprint and flexible form factor – compact to fit
within space constraints and can be configured differently for
local requirements.
Positive Grid Impact
- Improved grid reliability – clips fault currents completely
without de-energizing the downstream grid.
- Transparency to the grid – no discernable impact during
standby.
The technology has undergone substantial simulation, prototyping,
and testing. The company sees no significant technical barriers
and is on target to begin low-volume manufacturing and field
installations of three-phase commercial units within 12 months.
The Australian company was recently acquired as a subsidiary of
SC Power Systems, a US company, and operations have been moved to
the US. They've already engaged in substantive dialogue with
potential early customers and have validated the demand for its
first three-phase units (15KV, nominally 10KAmps/phase).
They've contracted with NEETRAC (see UFTO Note 17Jan02) to
prepare test procedures compatible with IEEE standards. NEETRAC
member utilities are lining up to be the hosts for utility field
tests scheduled for Q4, 2005. The company welcomes the
opportunity to explore application needs, and will be taking
orders as early as 2005.
Contact:
Woody Gibson, 415-277-0179 gibson@scpowersystems.com
SC Power Systems, Inc.
San Francisco, CA
Website: www.superconductors.com.au
The company is also raising equity funding. They presented at the
NREL Industry Growth Forum, Oct. 18-20 in Orlando
http://www.cleanenergyforum.com/. A business plan is available
from the company.
|
|